If I've asked before I give you my apologies now. But I'm wanting a roof over the mill and I've got poles in the ground and I'm doing a bit of this and a bit of that building style. I've tried using the calculators to figure out the technical strength of my poles and am hitting a dead end. I've tried using the beam calculator as well and come up with numbers that make no sense at all. I've visited with a few old builders who put things up according to acquired wisdom and whose buildings are still standing. My question is along these lines.
Poles are power poles with minimum 14" base diameter. They are currently rising to the sky some 30ft and will be trimmed to beam height. The poles are 20ft apart by design to allow 16ft lumber to move anywhere anytime. I need a beam to span 80ft total sitting on 5 poles 20ft apart. I've decided against trying to build my own beams as I just haven't found a beam design I can do that I'm happy with. So I can purchase Fir from BC or buy LVL here. Fir from BC I would just get 8"x24" and I'd be good but what about LVL? What do I need with that? I have the idea that a 2 ply 3 1/2"x18" would be enough but that doesn't fit the rule of thumb idea of an inch of beam for each foot of span. What say y'all?
Sizing the beam is straightforward. I'm assuming you are using 20' sticks but if you can do 40's in a built up beam you can weave the joints and make the connections over the posts stronger. What is your design snow load in lbs per square foot?
It shouldn't be too hard to check the posts for buckling under full vertical load.
Where I can't help is with lateral, that is a huge sail on top of tall posts, what is bracing that? Are there walls to provide bracing panels anywhere?
Snow load - According to jabacus my ULS is 31.4psf & SLS is 28.3psf
Rafters will sit on beams and be braced to poles as well as beam being braced to poles. Side walls will be closed in at some point, but not sure how quick. Roof will be tin. Poles will be trimmed down to create a 16ft ceiling. So approximate pole height is 14'6".
I fired that off too quick, may have done that a couple of times tonight.
Also think about up. With wind under it, that sail is pulling everything out of the ground and at every connection on the way to the tin, think that through as well. Up can get overall in the 15psf range, Chapter 3 of the codebook has some guidance there, then deduct dead weight from that and somehow tie the rest of that upward load to the ground.
Second thing was building width? ... let me show you, you can modify inputs
Assume 32' truss roof width on the building, 2' overhangs, each line of beams carries half of the weight. A 20 ' long beam is carrying half the 32' width plus the overhang, 18'. 20' of length supporting(x) 18' of width=360 square feet of roof supported by 20' of beam. 360 sf x (31.4 psf snow+10psf dead load) .. 360x41.4=14,904 lbs
I'm a rounder upper if we're that close, 15 kips
Load 15000
Span 240
play with dimensions
Fb #2 dougfir heavy timber 875, #1 is 1300, LVL 2800
E #2 DF 1.3, #1 1.6, LVL 2.0
Fv #2 DF 170, 170, LVL 280
You can change the width in that example to suit your real width and then play with the materials and sizes on the toolbox simple beam calc. Holler if you get stuck. And let me know what your numbers end up being, also the tip dia at 16'.
The calculator wants to know fiberstress, modulus of elasticity, and horizontal shear. I don't remember any builder I've talked to using those terms and I don't know what values to input. Span of building will be 40ft between beams with 2ft overhang on rafters. I'll use trusses.
Should this stay in thread or should I PM?
I'll shoot you a pm.
If y'all keep it in the thread more of us can learn!
Thanks. Feels better knowing I'm not the only one needing an education.
So correcting load numbers to a 40ft span and using Don's numbers I get to this.
Load becomes - 17,000
Span - 240
LVL Beam - I need 6" x 18"
#2 Douglas Fir - I need 8" x 22"
Did I do it right?
LVL I can buy locally but fir I'd need to source from Percy or something and then truck it here.
Hopefully y'all will check me :)
I didn't label those design strength values very well near the bottom of post #3.
Fb is the Fiberstress value the calc is asking for. It stands for "extreme fiberstress in bending". It doesn't mean "extreme" the way you're probably thinking, the extreme fiber in a beam is the strap of wood running along the top , or what we're looking at here is that strap of wood that forms the bottom edge. The extreme fiber is the furthest fiber away from the "neutral axis", the horizontal plane that would run along the center of the beam. A bending failure, which is what the Fb equation is looking at, would be when the fibers along the middle bottom of the beam begin to tear apart, splinter down, pop. So this part you must pass, it is a safety check. Yes there is a factor of safety built into that design value, that is why redneck dimensions usually sag rather than fail, they're some unkown depth into their safety and into the next check, deflection, sag.
The modulus of elasticity, E, is a check for stiffness. Rubber has great bending strength but isn't much of a beam, it is too elastic. I would limit deflection here to L/180, 1 inch in every 180" of span. Span here is 240" so limit your deflection to 1.33" (about 1-5/16") that would be under full snow load. As long as your Fb check and shear checks are looking good, on a building like this E is more of a judgement call but the more you let it slide the more those deflections start to become permanently set.
Fv, horizontal shear, as a beam bends the fibers along the bottom are stretching, the ones along the top are being compressed. Along horizontal planes within the beam the beam is trying to slip to accommodate those differing stretching and shrinking lengths. If those stresses get too high the beam splits down its length around the neutral axis usually beginning near or at the end supports but it can be at poorly thought out notches or holes. You'll find this is a concern mostly with short, heavy, heavily load beams. A church belltower support beam is the typical example.
So those were the design value inputs explained. The problem;
Tributary area for each 20' section of beam span is half the 40' span +2' o'hang =22'
Trib area= 22'x20=440 square ft
Design load= 440sf x 41.4 lbs per sf= 18216 .. ah you used the SLS 28.3+10psf dead load, ok, we'll go with the 17 kips
LVL comes 1-3/4" thick per ply, so a 3 ply is 5.25 for width. Ignoring deflection for the moment and rolling down throught the sizes hunting the failure, 14" fails, 16" passes, deflection is around 7/8", your call, it drops to about 5/8 at a triple 18" lvl. Your deflections will actually be a bit less if you buy 40'ers, stagger the seams over the posts and nail or preferably timberlock screw the plies together. This is an ag building I'd go with the LVL's, and they will do this math. Those suppliers of "engineered materials" have engineers on staff to check and/or stamp any of their products designs if you ever need it. I get lvls from my truss supplier who also engineers and supplies post frame buildings, if you do one stop shopping I'd run all this by their engineer. There's the beam math. I need to read up on poles. Bracing, can you weld?
Don is the guru here and is being very helpful.
I remember from when I studied this stuff a LONG time ago, that beam sizing is easy compared to working out the connection details. Also that the details are VERY important.
Guru, no, I'm just a carpenter who asked questions, feel free to comment on anything. You just made my sawmill lumber argument to the building inspector, usually the failure is at connections. This thing is big and open, and I saw the lake when I went to pm you, if you are looking across open water the wind has more fetch on you.
I checked manufactures and suppliers up here and I can get LVL in 3" thicknesses. I can make a 2 ply beam bringing that to 6". That is how I got it through the calculator to give me a pass on all 3 measures. I'm also able to get it in 80ft lengths if I'm willing to wait and pay the trucking. So if I can avoid the joinery at a reasonable cost that looks good to me. We have our own truck and a friend has a truss trailer so who knows what we'll choose to do. I'll need to add a bit of load on for the overhang. Forgot to do that. Regarding that wind lift; I will be closing in 2 sides of this as soon as possible. Our only wind risk here is when it comes from the east and that is not often. Still have to plan for it though. If I'm not mistaken 2 sides closed creates pretty good dead air space?
Thanks Don for your patient help getting me through the calculator and providing me with values I had no knowledge of. I'll come back to this as I progress.
I have had suppliers spec the beam for me before. This was with LVL's and or TJI's.
Didn't I read in your first post that 20' was the max. span? (5 poles @ 20' - 4 spans)
My local snow load (code) for trusses is 100#/sf.
Suppliers up here seem to always ask what the engineer has speced. This ain't engineered so he said he'd go with what i requested.
Yep, total length of 80ft. Not sure if i understand what your getting at?
4 hours north of me your in tundra country. No trees, no snow, not really much of anything. We are not in a high snowfall zone. We just have snow and cold for most of the year. ;D
Quote from: Grizzly on December 14, 2017, 04:40:53 PM
Grizz, your "talk" about getting an 80' beam and it's cost/trucking etc. through me off and you need to span 20'.... 4 times ;D
Having used LVL a bunch, but
not being an engineer, my "seat of the pants" feeling is that a 3 ply (std, 1-3/4" X 18") 18" tall beam would do the trick for a 20' span with your light snow load. I would buy 40 footers to "tie" the beam/post's, alternating the laps. (1st layer use 2-40 footers, 2nd layer start with a 20 footer, 3rd layer use 40 footers again) I would also (if your posts are wide enough at the beam location) notch the post to create a 5" (5-1/4" would be ideal) "seat" for the 3 layer beam to sit on with a 18" tall section of post on the inside to fasten to, further tying everything together. (make an "L" cut in your post top).
Now i gettcha. And yes, that will be the plan if a single 80ft proves to be more money than i like. One carpenter had the thought of using a steel cap on the pole with a saddle to place beam in. I like the idea but haven't really chased it yet.
Bracing the poles and beams is going to be the trick both in the plane of the beam and also in the plane of the trusses
For bracing on the rafter plane i was thinking of a brace that goes from about 4-6ft down the pole up across the rafter to about 1/3 - 1/2 way up the top slope. Is that about right?
That is beyond what I know. On smaller ones we've bolted through the post with 2@ 1/2" bolts, run up into the trusses at a 45 degree angle and nail very well to bottom and top chords of the truss. The bigger those triangles are the stronger it'll be.
You're describing what i want to do. I just didn't do it very well. (the description)
Quote from: Don P on December 19, 2017, 05:37:46 PM
I wonder if he needs all of his 20' spans @ full height or just at the log loading area? Even 2 of the spans with some stout 45's for bracing would do a lot, and for the truss plane. End walls would be just perfect along with maybe an added LVL (front to back) with another set of 45's.(diag. brackets/bracing/gusset) pick your local terminology :D in the middle.
I am not a big fan of setting something 18" tall on top of the posts unless it sits in a full depth welded steel saddle. The beams could be place between the posts with " joist hangers" or welded hangers. You would be handling less weight, make them up yourself , set them with a lift. You just need to cut the poles higher.
When they put the trusses on my barn they preassembled 4 trusses on the ground and raised them in place with a crane, 4 lifts took less than 2 hours to put all the trusses up.
711, i want a consistent ceiling height throughout so that i can drive loader/forklift/truck/whatever anywhere in the building. I also want 20ft openings everywhere for the same luxury of hauling wood wherever. Or at least until i start closing in the walls. But you had me thinking there for a while until i realized what i just said.
Holmes, good point. My carpenter was going to notch the poles and create a saddle of sorts but i'll see if he wants something stronger. With your idea of hanging the beams between the poles ....... I don't have 20ft logs to mill my own beams but i could get my rafter guy to make that style of truss to sit in that gap and into the fabricated truss hangers. And that could be a fair bit cheaper than LVL. I'm gonna check that out.
Quote from: Holmes on December 23, 2017, 08:03:34 AM
My daughter roughed this for me. Now, if that idea seems workable all I need is someone to help design a floor truss style of beam that I can build to go in there. Currently drawn for a 4" wide beam but can be done for almost any width.
(https://forestryforum.com/gallery/albums/userpics/28043/Beam_hanger_drawing_2.jpg?easyrotate_cache=1515351742)
I used to own a float house on ten mile lake , Oregon coast that was about 40' long 25' wide and had a 20' free span center beam for the front room. the beam was 40'. The structure was over 40 years old when I sold with no sag. The Beam was made using 20" x 8' 3/4" plywood sandwiched between 2"x10"s one above the other, glued and screwed together on each side of the ply, very stiff . we did not have much snow but high winds most winters. I would not be afraid of a 20' span between posts with a sandwich beam made like that. If you wanted more put 1/2" ply on the outside mismatching the ends.
Kinda hard for me to draw but If you could mount some 1/2" thick angle iron in a saddle of the pole and sit your beams on top of the angle and bolt everything fast to the pole that sure would make it strong.
(https://forestryforum.com/gallery/albums/userpics/39553/Angle.jpg?easyrotate_cache=1521417723)
In your mind push on the pole in each direction like a roof on an unenclosed building in the wind. Start welding bracing on that angle :(
Quote from: Don P on March 18, 2018, 09:24:33 PM
I agree 100 percent...
