Kiln Build

Started by DWyatt, August 30, 2023, 08:57:05 AM

Previous topic - Next topic

0 Members and 1 Guest are viewing this topic.

DWyatt

I am finally moving along with a kiln build at my new house. Dad's kiln box is getting tired and needs to be replaced. As a part of the build, I am also pouring a 4' x 44' concrete pad for air drying. I will preface this build with the fact that I understand that some of the things I am doing are overkill. The big cost is actually building this thing, the overkill is a small additional cost to ensure I don't have problems in the future. 

The kiln will be 10' x 16' outside dimensions with a 14' split door to be able to side load. Simple shed roof and ultra insulated to try to make this as energy efficient as possible. I am not doing a slab, I will put 2 layers of 2" insulation, then 2 layers of 3/4" plywood, glued and screwed together. 

Last night we got the air dry slab formed up and rebar installed. Again, the #4 on 12" centers is overkill, but I'm only doing this once. Digging footers on Thursday after work for the kiln and hopefully pouring everything next week.



 

scsmith42

What type of kiln are you building?  Solar, DH or conventional? (vacuum would not require a poured pad).
Peterson 10" WPF with 65' of track
Smith - Gallagher dedicated slabber
Tom's 3638D Baker band mill
and a mix of log handling heavy equipment.

K-Guy


For either DH or Conventional kilns the pad for the chamber cannot extend past the chamber walls because the concrete will work as a heat sink and you won't be able to reach the higher temperatures.
Nyle Service Dept.
A common mistake people make when trying to design something completely foolproof is to underestimate the ingenuity of complete fools.
- D. Adams

DWyatt

I should have included that in my first post. We currently have a Nyle L53 that sits in a homemade garage door panel kiln unit. I will be moving that to service this new kiln.

The long concrete pad in the picture will be only for air drying, having a flat space to put my pallets of air drying wood. The kiln itself will be 10x16 exterior dimensions. I will pour a footer then lay a block stem wall. I will then frame up walls just like a house and insulate cavities with rock wool then continuous interior polyiso that will overlay the block and connect to the floor polyiso. The floor will be filled with compacted screenings. then I will place two layers of 2" polyiso inside the block, connected to the wall polyiso. Then two layers of 3/4" plywood.

Here's my working sketch. I call it a working sketch because it's mostly completed, enough to get quantities, then I'll just build the thing and never finish the drawing.





doc henderson

you are sparing nothing.  I have studied but never built a kiln so take this for what it is worth.  I worry over time you may get settling and have not a flat surface.  would a concrete floor slab be more stable and last longer?  Well-sealed and maybe even protected by a sacrificial replaceable plywood cover?  with insulation and a thermal break at the outside wall of course.
Timber king 2000, 277c track loader, PJ 32 foot gooseneck, 1976 F700 state dump truck, JD 850 tractor.  2007 Chevy 3500HD dually, home built log splitter 18 horse 28 gpm with 5 inch cylinder and 32 inch split range with conveyor powered by a 12 volt tarp motor

DWyatt

Doc, I would normally worry about that, but my place is a bit unique. I am about 12" to solid limestone bedrock on my property. I don't think that there will be much settlement. 

DWyatt

Footers are dug! The pictures are before we were done, it got too dark for pictures. Rock depth ranged from 36" to 10". We went ahead and dug out the center too since it is such a small area and it was all falling in anyways. 

You can see the area where the rock was 36" deep. It was about a 3' wide area.


 


This whole side was the shallowest, about 10"-12" to rock. 


 

K-Guy


The maximum chamber size for a L53 is 8 x 13, you will have trouble heating it and you are reducing airflow by going 10' deep.
Nyle Service Dept.
A common mistake people make when trying to design something completely foolproof is to underestimate the ingenuity of complete fools.
- D. Adams

DWyatt

I do appreciate the heads up on that. Inside dimensions will actually be 8'-5" x 14'-5", so not terribly oversized . I already plan to install 4 additional  auxiliary fans, which our current kiln chamber has, and from what I've read is necessary for uniform drying. As to the heating aspect, I will just have to wait and see. If I have issues, I will add auxiliary heat as well.

DWyatt

Since the rock is so irregular around here, I fill footers to somewhat level using 411 stone. 4" lifts, water then compact. Rinse and repeat. Footer is just about ready to pour. Got the inside formed and electric ran over the weekend also.



 



 

DWyatt

Concrete is poured! Stripped forms last night and this morning and started filling the middle up with stone. I'll take stone to the top of footer then the guy I'm having lay block can get started. The footer is way thick, but if I didn't do that, I would have had to add an extra course of block, plus I wouldn't have hit minimum load size which would have cost extra.

Only a few dog prints  :D



 



 

DWyatt

Footer is backfilled and ready for block. Teaching the kiddos how to run the compactor and had our 10 yo help with getting things laid out and chalk lines snapped  :)



 



 

mudfarmer

Very nice, do you have the air drying sidewalk filled up yet?  ;D we have been working on more/ better pallet bunks but should have been smart like you and just poured a slab!

DWyatt

Finally got my block mason here today and he got all of the block laid. You all get to view it with a flashlight just like I did after working a 14 hour day today  ::) 

Time to backfill this weekend



 


Tom K

Good to see some progress. I'm following along a few miles East of you with a vested interest. I need to do something come spring, still debating between a solar kiln or a DH kiln with a L53. Looking forward to see how you like this when your done.

DWyatt

Tom, I hope you don't get bored following along at my speed. My day job business is absolutely slammed, and we've got 4 kids. That doesn't leave much time to work on my extracurricular projects. If everything goes well, I will have this done by the end of the year. 

DWyatt

Got the tractor to the house and moved my cut lumber to the air drying spot. Progress is progress  :D



 

DWyatt

As promised, the progress is slow. I am building all of the walls in the shop then I will set them with the tractor. Building 16' walls in the shop means that everything is a wreck and everything is shoved to the back. I have the two long walls built, just need to make the short ones this week then maybe I can set walls and trusses this weekend.



 


DWyatt

Another little update. I finished up building the last wall last night. Just have to put the sheathing on it tonight. Unfortunately, it looks like this weekend is going to be a washout. Hopefully there is a lull in the rain long enough to get these walls stood up. The last wall has my access man door so I don't have to open the big door to check on things. The bottom plate will get cut out once I set the wall on the foundation.



 

DWyatt

Walls are standing! Dad came over and helped yesterday with the tractor, it took about 2 hours. That 2 hours included 17 trips from the kiln to my shop to get that one last tool that I forgot  :D 

Got the second top plate up today between rain and started to get things prepped for trusses including cutting and marking all the purlins so setting trusses will be quick.



 

DWyatt

Trusses are set. I was able to get off work a couple hours early yesterday and Dad came to help. Took about 2 hours. Just have to get the overhangs/facia finished up then it's time for metal. Overhangs save buildings, 2' minimum.



 

barbender

I agree, I'm a big fan of wide overhangs too. Looking great! 
Too many irons in the fire

Andries

Good Excellent "cap and shoes"!
That one will stand the test of time.
You're in NWOhio - the walls are 2x6 so plenty of room for insulation there. What have you got planned for floor insulation?
LT40G25
Ford 545D loader
Stihl chainsaws

DWyatt

@Andries the walls are actually 2x8 which will allow me to do an r30 Rockwood batt. Then I'll put 2 layers of polyiso then plywood. The polyiso will be my air barrier and all joints will be taped. The upcharge to go from 2x6 to 2x8 was insignificant so I decided the more insulated the better, especially when trying to dry during the winter.

The floor will be 2 ea 2" layers of polyiso with 2 layers of 3/4" plywood over top. I am avoiding a concrete slab with my design. 

Andries

Nice!
2x8 and the polyiso are a solid way to go.
As DocH said: you are sparing nothing. 👍
LT40G25
Ford 545D loader
Stihl chainsaws

DWyatt

Made some more progress this afternoon. What a beautiful weekend we had! Got the rest of the sheathing on and got about half of the subfacia boards on. 

I was even lucky enough to have my favorite helper for about an hour. Evan got a new tool set for his 3rd birthday yesterday and he was determined to use it! 



 



 



 

K-Guy

I wouldn't use R-30 insulation, your kiln will overheat in the summer. No more than R-26.
Nyle Service Dept.
A common mistake people make when trying to design something completely foolproof is to underestimate the ingenuity of complete fools.
- D. Adams

DWyatt

@K-Guy Isn't that the purpose of the powered and passive vents? If the kiln chamber heats up too much, the power vent fires up and exhausts? ???

K-Guy


If your kiln is too well insulated the vent will vent too much and you control of the drying. Ideally, when drying hardwoods, you would never vent as then the kiln controls the drying completely. For softwoods it doesn't matter, that is why many people don't dry oak in the summer as it is too hard to control the drying and temperature.
Nyle Service Dept.
A common mistake people make when trying to design something completely foolproof is to underestimate the ingenuity of complete fools.
- D. Adams

DWyatt

Progress again! Saturday morning I picked up all my metal trim pieces and metal for the roof. I finished building out the overhangs Saturday afternoon. Sunday Dad and I got all of the metal on the roof and I got most everything wrapped in house wrap. I have to get all of the trims up this week so I can get measured for metal and have it here over the Thanksgiving weekend. 



 

Do you know how far away you have to stand to see the metal on a 2:12 roof so I can prove that I made progress? About 50' :D



 

DWyatt

I made good progress over the last week, but not anything that is going to show well in pictures. I finished the house wrap on the end walls, put in some misc blocking between the trusses, and installed the treated door jambs. I also got all of the F&J trim installed so I could get measured for metal. Metal should be showing up today or tomorrow so hopefully I can get it all installed over the long weekend. Yesterday I got all the lumber and hinges to build the doors. 

This getting dark at 5:30 PM means I go to work in the dark and come home in the dark. Getting things put together with a work light and headlamp makes things take so much longer. Luckily I'll be able to build the doors in the shop then lift them into place. 

teakwood

it was after i had erected the structure of the kiln and started getting into details visible progress slowed down considerably and i told myself, dang is it alot of work to finish a kiln built. i think i did mine in 3 full work weeks  
National Stihl Timbersports Champion Costa Rica 2018

DWyatt

I am to the point now that if I had a full week to work on things, it would be done. I am hoping to get a lot done over the long Thanksgiving weekend. 

Had the initial filling of a new water tower contract that I'm running the last two days, then a late preconstruction meeting today. Going to be knocking on 40 billable hrs in my three day work week. Needless to say, not much has been done the last 2 nights. 

DWyatt

Big progress made this weekend. Between Thanksgiving gatherings and spending time with the family, I got quite a bit done. I was short on my soffit order so I wasn't able to finish it and I was shorted the two long pieces of metal for the front of the kiln. My primary work hours this weekend were from 6am to 9am while everyone was still asleep. I should get it all finished up next weekend. 

When I have another project like this, I'll be investing in a suspension tool belt. Working off a ladder for all the soffit and facia with a toolbelt hanging on, my hips are shot! 64 trips just to do the soffit.  :o



 



 




barbender

It looks great!👍👍
Too many irons in the fire

Peter Drouin

A&P saw Mill LLC.
45' of Wood Mizer, cutting since 1987.
License NH softwood grader.

DWyatt

It was a slow weekend, partly because I forgot to order the material and partly because we had a lot of stuff scheduled. I did get the rest of the trim put around the big door and the metal put on the front (minus the one piece that I am missing). The final piece of metal and remainder soffit is supposed to be in today which will mean I can put it on this weekend. Hopefully I can get the doors built this week and ready to hang next weekend. 



 

doc henderson

It looks very well done.
Timber king 2000, 277c track loader, PJ 32 foot gooseneck, 1976 F700 state dump truck, JD 850 tractor.  2007 Chevy 3500HD dually, home built log splitter 18 horse 28 gpm with 5 inch cylinder and 32 inch split range with conveyor powered by a 12 volt tarp motor

DWyatt

Forgot to post an update after the weekend. I've been absolutely slammed at the day job with several late meetings so progress has been slow. Over the weekend I did get the big doors built. They're probably over built, it's my style, but the 5 ea 10" strap hinges should hold things well. Planning to get them mounted this coming weekend.



 

doc henderson

I assume the sagging out of square will be mitigates with sheathing and or some diagonal braces, cable or otherwise?
Timber king 2000, 277c track loader, PJ 32 foot gooseneck, 1976 F700 state dump truck, JD 850 tractor.  2007 Chevy 3500HD dually, home built log splitter 18 horse 28 gpm with 5 inch cylinder and 32 inch split range with conveyor powered by a 12 volt tarp motor

DWyatt

Yes. The exterior will have metal, not technically bracing,  but there will be 6 rows of screws, so that's something. The interior will have sheathing. I bought 1/2" treated ply for the interior, but I am probably going to elect to change to a 1/4" ply and nail at 6" centers. After carrying the 1/2" treated ply, I can't convince myself that the extra thickness will provide more bracing than the weight will hinder. Dang that plywood was heavy.

As they are currently, without any bracing, I am able to stand them up on a corner and bounce them. When I lay it back down it's still perfectly square. Not proper testing procedures, but it's my sledgehammer test  :D

doc henderson

I think that is what 90% of us would do too.  so that is great, but after a few years of hot and cold, and with humidity blah blah blah.  could glue and screw your plywood with TB3 or construction adhesive.  that means adherent every inch of the frame.  I think that will brace it well.  you could incorporate a diagonal cable with a turn buckle for some tension and adjustment over time.  from the top hinge area to the opposite corner at the bottom where the doors meet.  I assume the metal you speak of on the outside is the siding.  I agree that would be less likely to keep the doors from sagging.  great start so far. 
Timber king 2000, 277c track loader, PJ 32 foot gooseneck, 1976 F700 state dump truck, JD 850 tractor.  2007 Chevy 3500HD dually, home built log splitter 18 horse 28 gpm with 5 inch cylinder and 32 inch split range with conveyor powered by a 12 volt tarp motor

DWyatt

Doc, I do like the glue idea and will probably do that. With the frame being beefy, I could easily install a cable on the interior face of the door to be adjusted as needed. Since I have the block wall and footer at the door opening, my intention is to install a small block where the two doors meet. That would keep tension off the hinges when they are closed, which is 99% of the time.

teakwood

That's what i did! but now they are hard to close sometimes  :D
National Stihl Timbersports Champion Costa Rica 2018

DWyatt

@teakwood Do you have some kind of plywood on the inside to prevent sag?

teakwood

Nope, lumber frame then filled out with styrofoam panels 1" and then tyg boards nailed to it inside and outside. All this is way sufficiently to prevent sagging

https://forestryforum.com/board/index.php?topic=121021.40
Reply #48
National Stihl Timbersports Champion Costa Rica 2018

Oth

My doors have 1/2" T-111 on the outside and 1/4" plywood on the inside. No diagonal bracing, no glue. Haven't moved at all. Not sure how big yours are, they do look a bit larger though. I wouldn't bother with the glue though, most construction adhesive dries pretty *DanG hard and with the amount of expansion and contraction in the materials from heating and cooling down I'd bet the glue joint would fail sooner than later. Cable with a turnbuckle is a good idea but I bet ya never adjust it if it's got proper sheet good sheathing on each side.

doc henderson

If I were going to use boards, I would consider installing on a diagonal.
Timber king 2000, 277c track loader, PJ 32 foot gooseneck, 1976 F700 state dump truck, JD 850 tractor.  2007 Chevy 3500HD dually, home built log splitter 18 horse 28 gpm with 5 inch cylinder and 32 inch split range with conveyor powered by a 12 volt tarp motor

Sod saw

.


Doc has two good ideas for the door.

Plywood is a great idea instead of boards.  I used thin Luan plywood that is used for under vinyl flooring.   Cheap, light weight, and stiff with proper frame.

Using high strength construction adhesive (from a tube) works well to bond the plywood to frame but be sure to use deck screws as they are coated for outdoor weather and we all know how the inside of a kiln gets.  Hot and humid.

When installing foam board into the doors and walls, spray foam the edges of all foam boards to seal to the studs and framework.   At 150 degrees (F) a lot of heat is lost thru the smallest space.

Nice looking structure.


.

LT 40 hyd.          Solar Kiln.          Misc necessary toys.
.
It's extremely easy to make things complicated, but very difficult to keep things simple.
.

DWyatt

It's been awhile since I updated you all on the kiln. So I've got a big photo dump to do. Doors are mounted and functioning, the entire kiln is insulated (except the floor), and I'm going to be starting the interior plywood this week!



 



 



 



 



 



 

DWyatt

What a week it's been. Over the last 8 or 9 days my wife, myself, 3 yr old, and 8 month old all caught the covids. Let me tell you, an 8 month old cutting teeth and having covid was like living in hell. We are all on the mend and I still managed to get quite a bit done on the kiln. All the plywood is hung inside and it's time for the floor. I am not sure how well it will come through in the pictured, but please take a moment to appreciate my perfectly chalked lines on the doors for my screw pattern. I put all of the 1/2" plywood on the ceiling by myself. Wow is that stuff heavy when you're 4 steps up a ladder, but I only dropped 2 sheets.



 



 



 


DWyatt

Stone is in and compacted. I decided that it wasn't worth going to get the tractor from my parents and that I was just going to wheelbarrow it. 2 hours later I was regretting that choice  :D Last thing to do is screed off the sand, then I'll start getting the foam and plywood down.



 

DWyatt

Got the sand all knocked down around 10:30PM Friday night. Used my 8' level and laser to screed off the sand. Now if this 40 MPH wind ever lets up, I'll get the foam down. 



 

DWyatt

The floor is in and about half the seals are installed. Unfortunately my small door was about 1/8" too big, it's so hard to predict the hinge swing on a door that 5" thick. And the more unfortunate part is that I have it all made and trimmed out with metal and the only way to fix it is to completely disassemble it and cut an 1/8" off then put it all together  smiley_thumbsdown  hopefully work is less hectic this week and I can get more done. 


DWyatt

Back to square 1 with the small door. Had to take it 100% apart to cut 1/4" off of the width, then put all the trim back on. It'll get hung this weekend.Snapchat-934900079.jpg

DWyatt

I got the electric pulled and hooked up to the kiln. I ended up just jumping a 50 amp subpanel to the kiln and stuck another ground rod in. Cheap insurance, I suppose. The baffle is installed and the inside park of the l53 is installed. My exterior rated box should be in next week, then I can get everything hooked up. If I could get a weekend that wasn't 40 mph winds and raining, I could actually get this thing finished.





barbender

 I do believe the electrical code specifies a 4 wire service (if you are running 220 volt out there) in any case a dedicated ground is supposed to be run back to the main panel, and also tie in to a ground rod like you have. Kind of "double grounded" in a sense. When I was building, the electrical inspector told me that the line of thought is to have a ground running back to source so that power doesn't end up grounding through a propane line or something.
Too many irons in the fire

YellowHammer

Or through the building, I've seen a guy get knocked to the ground when he grabbed the doorknob on a metal building. 

Yes, if you are going to wire to code for insurance reasons, the NEC requires 4 wires run from a service panel to a sub panel, two hots, a neutral, and a ground wire.  The neutral wire, ground wire and ground rod wire are all bonded to the service panel through the ground bar, and the ground rod must be within 6 feet of the service panel. So 3 wires bonded to earth ground at the service panel all tied together.

The sub panel should have separate neutrals and grounds, and not have bonded ground to neutral and no ground rod at the sub panel.  However, the kiln unit itself, (end machine) can be tied to a ground rod directly to its frame for lightning protection.

You may also consider a lighting protection or surge suppressor panel breaker mounted in your service panel, they take a 220V breaker slot.

Anyway, I'm not the Electrical Code police, just agreeing with Barbender. 

 
YellowHammerisms:

Take steps to save steps.

If it won't roll, its not a log; it's still a tree.  Sawmills cut logs, not trees.

Kiln drying wood: When the cookies are burned, they're burned, and you can't fix them.

Sawing is fun for the first couple million boards.

Be smarter than the sawdust

DWyatt

You are both correct. The electrical supplier I use helps me through my limited knowledge of the electric code. Anytime you are running electric after the first means of disconnect, you carry the ground. My first means of disconnect is at my 400 amp meter base. There are 2 EA 200 amp breakers. One feeds the house and one feeds the shop. The ground is carried to both, then carried to a couple of sub panels. The sub panel I purchased did not have separate neutral and ground bars so I have installed a separate ground bar to the panel. 

I appreciate the insight and while I am not in a inspected county, I try to do things correctly. Luckily a good friend of mine is an electrician and owns his own residential/light commercial electric company so he helps me work through any questions I have. 

@YellowHammer I do have a question about one of your comments that I should not have a ground rod at the subpanel that I believe differs from my understanding. My understanding that since it is a subpanel, the ground is carried to the panel and the ground and neutral shall not be bonded at the panel. As long as these conditions are met, a ground can be added at the subpanel. Youtube video below from Electrician U that I believe explains what I understood.


doc henderson

our pool has everything bonded to ground.  that include the lights grounded to the wire mesh under the concrete, and back to the panel with a wire to earth ground.  you want that breaker to snap if any current goes to the wrong place.  all the grounds and neutral/common wires go to the same bar in my main panels. you can have current feedback via a ground and thus to the metal part of a tool.  In a tornado you could have a pole go down and in theory lose neutral but not the 120-volt legs.  Do it right.  the question sometimes "what is the right way".
Timber king 2000, 277c track loader, PJ 32 foot gooseneck, 1976 F700 state dump truck, JD 850 tractor.  2007 Chevy 3500HD dually, home built log splitter 18 horse 28 gpm with 5 inch cylinder and 32 inch split range with conveyor powered by a 12 volt tarp motor

NCWoodsGuy

Nice kiln build!

Not sure about swimming pools but my experience is only the first (main) panel where power comes from the utility is to have the ground and neutral bonded. All sub panels that feed from that main shall have the ground and neutral separate, as someone posted above. Local codes may vary of course.

Odd local variation here in my part of NC is the service entrance main requires two ground rods spaced 6 feet apart. I thought that was weird.
Woodland Mills HM126 16'
Kubota L4710
Kubota L2250

doc henderson

I know some soil types offer better ground, and moisture plays a role.  maybe a safeguard in case a wire breaks or comes disconnected.  I think it ends up the same if the main is bonded together, it all acts the same.
Timber king 2000, 277c track loader, PJ 32 foot gooseneck, 1976 F700 state dump truck, JD 850 tractor.  2007 Chevy 3500HD dually, home built log splitter 18 horse 28 gpm with 5 inch cylinder and 32 inch split range with conveyor powered by a 12 volt tarp motor

Larry

When I worked for the phone company I learned lots about earth grounds. Most equipment installations at minimum, required three ground rods in a specific pattern for protection from voltage surges. Once the ground rods were in place we used something called a megger (ohm meter on steroids) to measure ground resistance. It was interesting to see the results as some failed.

When I moved to Arkansas I learned of a grounding system far far better than a rod. Its called a Ufer which is a ground wire tied to the building rebar. I made this discovery because our soil has a rock or three which tend to make driving ground rods difficult. :veryangry: :huh?

More than ya ever wanted to know about ground rods.
 
Larry, making useful and beautiful things out of the most environmental friendly material on the planet.

We need to insure our customers understand the importance of our craft.

YellowHammer

The video is pretty good, and he may be 100% right, but believe there is some ambiguity of the NEC that causes confusion, and I may be wrong, the inspectors may be wrong or who knows, and although the NEC can be considered minimums, apparently my inspection department takes them as absolutes.

I failed an inspection several years ago because my Licensed electrician had grounded my service panel, my sub panel but not my equipment (planer).  The 4 wire branch is called an equipment ground for a reason, I was told by the inspector, and so we removed the sub panel ground rod wire, and grounded the planer with it's own ground rod and we passed.  I was told the equipment had to have a ground rod, but not the branch panel, and not both.  Either way, when we removed the branch panel earth ground rod wire, we passed. 

We just wired up a mobile home, and when the installers set the home, the only ground rod was to the main service disconnect at the pole.  I questioned the inspection department about this, and they sent me an inspection packet, which included this cute little drawing of a 4 wire in conduit, with no ground at the mobile home interior branch panel.  The document had several pages and the diagrams of the service panel were quite detailed about grounding. 

Reading from NEC code  250.32(A)Exception:  A grounding electrode shall not be required where only a single branch circuit, including a multiwire branch circuit, supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the normally non current-carrying metal parts of equipment.

So in this case it's not a requirement, and in my case, my inspectors read this as if it's not specially spelled out as a requirement, then doing anything different violates the NEC requirement.

So anyway, if you Google it there is lots of confusion, but seems to me the more ground rods the better, until I failed my inspection...

I do know that in the equipment testing world, putting too many ground rods in is a definite "do not do" golden rule, as it causes tremendous ground loop errors that is easily picked up by our test equipment.  Basically, the golden rule in the testing world is "ground once, and ground at the source."

So, I guess the answer from me is if I had my old job, I could just call up the head of the Director of the NEC and ask him, but now all I can do if read the codes and get failed by the inspectors for putting in too many grounds, wrongly or rightly.  ffcheesy ffcheesy


YellowHammerisms:

Take steps to save steps.

If it won't roll, its not a log; it's still a tree.  Sawmills cut logs, not trees.

Kiln drying wood: When the cookies are burned, they're burned, and you can't fix them.

Sawing is fun for the first couple million boards.

Be smarter than the sawdust

Sod saw

.


Glad to hear that you are ready to finish up, hope that you get good weather.  I am still messing with door seals even after a few years of use.  What did you find best for gasket material, weather seal?

Yellowhammer, When I build electrical systems I need to know what the "system" is going to be used for.  In the case of radio/Tv station or recording studio or large computer systems or equivalent, then your observation about having only one ground source is absolutely correct.  Ground loops will  drive you nuts.

Doc.  Your pool observation is also correct as far as the code goes.  Everything metal must be bonded together.  There are different engineering (physics) reasons than for an electrical service entrance.

Now let's look at the National Electrical Code itself.  When an installation is prohibited the language in that section of the code will reflect that.  When an installation is required, the language in that section of the code will reflect that also.  

Now the gray area:    When an installation is not specifically prohibited (such as an extra ground rod someplace), then you can do it if you wish but you can not ignore other required sections of the code.  

Perhaps as an example (let's use our imagination for a moment) Yellowhammer has a 3 phase planer that has new wires from a sub panel to feed their new planner.  Let's assume that the electrician ran only 4 conductors to the planner control box.  3 hot wires and a neutral.  In this example the inspector is correct in saying that the planer steel frame needs grounding.  A ground rod is ok and/or another 5th ground wire run back to the sub panel is ok.  Yes you can install a rod and the 5th ground wire at the same time. The gentleman on the video is correct, the code does not prohibit a ground rod along with a separate ground wire to the panel (sub panel).

I disagree with Yellowhammer's inspector where he had the ground rod removed from the sub panel.  UNLESS it was for ease and convenience of connecting to the planner with the minimal of work and expense.  I was not there but have run into inspectors who require something because they misunderstand the intentions of the language of the code as pointed out above.   And sometimes I misunderstand too and need help with clearing up code intentions.

Let's look at sub panels- - - - If a sub panel is within the same building as the main service entrance panel, then that sub panel must have: neutral wire, the hot wires (2 or 3 depending on phases) and a separate ground wire in the same runway connected to the ground in the main service entrance panel but connected to its own ground buss within the sub panel.  Within that sub panel the white neutral (not always needed) will be connected to its own buss insulated from the ground buss.

Oh, by the way, one question on our electrical license tests;  What color is the green ground wire?

Now on to an exception to the grounding of sub panels. I hope that this does not confuse folks.  If you have a main service entrance panel in a building (house as an example) and you have an out  building that you wish to run wires to,  You can treat that out building as though it has its own main service entrance.  In other words the code does not require that a separate ground wire be run to that building.  But as stated above, the code does not prohibit a separate ground wire to bond that panel in the out building to the main panel in the house.  Without that separate ground wire from house to out building panel, you will need two ground rods in the out building, just like you need two points of ground with the main service entrance.  And yes, if you believe that the earth will not conduct electricity well, you are correct that you can always add more rods further and further apart.

Having explained that exception, I always run a separate ground wire from panel to all sub panels, regardless of whether it is in an out building or not.  Ground rods can be extra if you wish.

When dealing with audio, video, computers etc.  All equipment should be bonded to only one common ground location, and not the lightning system.

Larry's grounding to rebar is great if you have it.  Not many pole barns or houses have access to it.  The National Electrical Code requires only two rods for Electrical Service Entrance in most cases.  More can be added if poor grounds are noted in that area.

A note here about storms and the loss of the neutral connection from the service entrance at the building to a pole.  I have been asked to repair many major ice storm damaged homes because the ice brought down only the neutral wire from the pole to the house.

Without proper ground rods (or bonded copper water pipe from street to house). Those houses had 240 volts flowing throughout the whole electrical system.  Any appliances that were "on" got fried. Except for appliances that were designed to operate on 240 volts.   Light bulbs blew, kitchen  appliances died, refrigerators died, cloths washers, stereo, GFI outlets, you can fill in the blanks here.  My point is that even new services can have corroded ground connections or weak conducting ground paths to the dirt.  And don't overlook the utilities outdoor connectors from pole to building.  They have the pleasure of being out there in all kinds of weather and temperature changes.

Gas lines should never be the source of grounding.

have fun but be safe


.
LT 40 hyd.          Solar Kiln.          Misc necessary toys.
.
It's extremely easy to make things complicated, but very difficult to keep things simple.
.

Sod saw

.


Having just studied the drawing shown by Yellowhammer in his post I find that they would violate all of our Electrical Utility requirements as well as the National Electrical Code.

The reason for this note is to illustrate the different requirements in different areas of the country.

Your drawings show 2 inch diameter electrical conduit from the meter area to the mobil home.  At the meter area where that PVC (plastic) conduit connects to the pole box, your conduit connects directly to the box.

Here in NY State, we have been know to have winter freezing the ground to about 4 feet deep.  As we all know, when water freezes it expands causing the surface of the earth to rise up forcing the electrical conduit to jam its way into the box breaking fittings and bending boxes.   When the ground thaws it settles to below the original elevation of last fall causing the electrical conduit to pull out of the box on the pole.  

How to solve tis issue?

We are required to install a slip joint where the conduit joins into the box to allow the ground to move the conduit up and down without stress on the conduit pipe or the wire connections within the box.

Just a detail but important to the area where you live.  

Oh by the way, I have never used those flexible pipe hose things under trailers .  I should think that they work well for you where the trailer might bounce on its springs, or the ground settles.

Question:  Did your electrical company drawing omit the caution tape over the pipe under ground?


.
LT 40 hyd.          Solar Kiln.          Misc necessary toys.
.
It's extremely easy to make things complicated, but very difficult to keep things simple.
.

YellowHammer

Lots of info to digest for sure!  I love it.  

I reviewed the NEC codes I could find, and they are pretty ambiguous and poorly worded.  For example, as far as I can tell, in 2023 the section 352.44(B) was added which requires expansion fittings to be installed above grade when direct buried PVC conduit emerges from the ground and compensation is needed for earth settling or movement, including frost heave.  So what is meant by compensation for earth settling?  Compaction by a mechanical or man powered tamper?  What else could be done to not require compensation for earth settling?  I could argue that I could fill in the ditch with 100% washed compacted gravel and then I wouldn't be in violation?  I hate ambiguity in technical codes and documents.

Prior to that, the table 352.44 states PVC expands 3.65"/100ft for 90°F temp range, which means any run longer than 6.85' requires an expansion fitting, however, with the drawing by the county, with the 18" bury depth of the conduit, and the placement of the weatherproof disconnect, then the vertical run of the conduit won't exceed that, so would meet code.  However, it would not meet code based on the 2023 update, assuming that I filled with uncompacted dirt, but if I backfilled the ditch and compacted the clay, then I would meet code. 

Also, as far as I could see, the requirement for marking tape is describes in NEC 300.5 (3) where it states "Underground conductors buried 18" below grade shall have making tape" and even though the county didn't require it as far as I could tell, I run it as a routine step whenever I l trench wire or water.  I have a little transmitter/tracer that I can send a signal down conductive marking tape, and find it.

Either way, the inspectors in my county have the final word, and what they say is law and I couldn't get insurance for my two kilns or any of my operation until I passed inspections with the code cops and the yearly Fire Marshall inspections.      
YellowHammerisms:

Take steps to save steps.

If it won't roll, its not a log; it's still a tree.  Sawmills cut logs, not trees.

Kiln drying wood: When the cookies are burned, they're burned, and you can't fix them.

Sawing is fun for the first couple million boards.

Be smarter than the sawdust

DWyatt

I love all this information, mainly because electric is something that I know enough about to be dangerous.  I can however follow directions really well which is why I ALWAYS consult with my electrical supplier (and his son who is licensed) as well as my buddy who is an electrician. I normally leave these interactions with saying that there are specific reasons why my PE is as a civil engineer. I can see everything I work on, which is not the case when working with electric.

I live is an unzoned, no inspection township within my county. I am doing all of this work as an individual for my own use, not as a business. While I thoroughly enjoy that I don't have "the man" to deal with when I want to put up a new building, I would love to have more guidance when it comes to electrical. From the sound of things, the NEC is left widely open to interpretation on many items. Even if I had an inspector, they could say completely different things than Yellowhammer's inspector when it comes to this topic in particular. 

Grey areas, kind of like the spelling of gray are well...grey...or gray. My mind works much better with black and white. 

My goal with not only this build, but any build is to build things in the correct manner. I am not going to cut a corner in an attempt to save a few dollars. Electrical systems, if done incorrectly, can be devastating. I thoroughly appreciate all of the insight on this subject!

DWyatt

Quote from: Sod saw on March 19, 2024, 05:20:53 PM.


Glad to hear that you are ready to finish up, hope that you get good weather.  I am still messing with door seals even after a few years of use.  What did you find best for gasket material, weather seal?

.
I am using a combination of gaskets on the doors. I think I about bought Lowes out of weather stripping when I was there. Along the hinge side, I have two rows of seals that are 3/8" - 3/16" seals. Along the top, I mounted a 2"x2" aluminum angle that has the same seal that the door will press against when latched closed. The bottom of the doors will seal against the floor structure. For that I got seals that expand from 1" - 3/8" which will be mounted on the face of the floor framing. For the gap between the doors, I am using the same thick seals that will smash together as the doors close. The big door on the kiln also faces NE which should help keep it out of the weather as much as possible. The goal is to challenge the seals as little as possible.

DWyatt

Conduit and wire is installed. Just have to finish things out. I have the box for the controller. Just need to install it, then I'm ready to run the first load! Oh and I also got the small door installed, but it was too dark for a picture.

PXL_20240330_021445246.jpg

blackhawk

Maybe you haven't gotten that far, but I would suggest having 4 extra fans instead of 2.  I needed that to get the air speed up through the stack.  I did my extra fans at 90° instead of at an angle.  I didn't try them at an angle, so I'm not sure if there will be a difference.  One thing that Stan suggested was to put a 45° angle piece of plywood along the wall/ceiling opposite the fans.  When the fans hit that sharp corner a good amount of air gets deflected back.  The angled piece helps push the air down that far wall and then through the stack.  I tried it both ways and it did make a significant difference.  If you don't have on already, I suggest getting an air flow meter.  I have a Kestrel brand and it really helps to check your airflow through the stack and be sure it is even.  
Lucas 7-23 with slabber. Nyle L53 kiln. Shopbot CNC 48x96

DWyatt

Thanks for the heads up. I had planned to run the kiln with the two auxiliary fans, but I spaced them toward the edge of the stack so I have room to add two more if needed. Yes, on the deflectors. I haven't added them yet, but I plan to. I appreciate the reminder!

I am basically ready to run the first load. This weekend I finished getting the power cord run into the kiln unit, got all the seals put on the small door, finished the electrical, and installed the cam lock trailer door latch on the big door. I have to put the seal on the bottom of the big door, get my 45 degree angle pieces installed at the top corner of the wall, and mount the wet & dry sensors. I can finally see the light at the end of the tunnel!  ffcool

Magicman

This is getting Exciting... :thumbsup:
Knothole Sawmill, LLC     '98 Wood-Mizer LT40SuperHydraulic   WM Million BF Club Member   WM Pro Sawyer Network

It's Weird being the Same Age as Old People

Never allow your "need" to make money to exceed your "desire" to provide quality service.....The Magicman

K-Guy


Unfortunately your electrical will all have to be redone, it must be in water tight boxes and be in aluminum or plastic conduit. The steel will quickly rot due to the tannic acid in the wood.
Nyle Service Dept.
A common mistake people make when trying to design something completely foolproof is to underestimate the ingenuity of complete fools.
- D. Adams

DWyatt

K-Guy, you're probably right. Dad's kiln has been in operation like this for 25ish years and never had an issue. So if I have to redo things every 25 years, I'm okay with that.