how to eliminate water hammer

Started by stratford 50, February 10, 2010, 06:56:42 AM

Previous topic - Next topic

0 Members and 1 Guest are viewing this topic.

stratford 50

Installed e- classic fall of 2008 tied into system 2000 oil furnace, seem to have lots of water hammer on all 5 zones, changed  1 zone valve and installed a variable speed circulator but still hammering.  Any suggestions would be helpful.

Thanks,
Stratford 50



beenthere

south central Wisconsin
It may be that my sole purpose in life is simply to serve as a warning to others

zopi

get the air out and maybe add an expansion/surge tank...
Got Wood?
LT-15G GO chassis added.
WM sharpener and setter
And lots of junk.

Jasperfield

I'd add an expansion tank. You'll need it time & time again.

coyotebait

elbows with bleaders at highest area of each zone . Or at each register. When they start hammering crack them a little till water comes out then close ,when done add water to the system to make up room for the lost air.

slowzuki

If the zone valves open or close too fast with a high flow pump you will get hammer too.