With the L53 unit, if you exceed about 133 degrees, you will trip the compressor. There is a high temp limit at which you can run the compressor. If you exceed 133 to heat up the kiln to 145, then turn the compressor off before you exceed 133 degrees DB. Once you cool down below 130 degrees, you can turn it back on. You might want to partially open the vents so that the water vapor can exit the unit while the compressor is shut down. If you trip the compressor, you have to take the side panel off the unit and hit the re-set button which is located on one of the refrigerant lines. At wood moisture content of 12%, I run the DB at 125 degrees and the WB at 75 degrees to ensure the humidity is at least 3% EMC drier than the MC of the wood.