I thought I wanted 240V ?? Is there an upside or downside to 208v versus 240v ?

Southside

Well technically 240V would draw less for the same work, but it would not really be an appreciable number.  The important thing is what voltage your motors are set up to run at.  
Franklin buncher and skidder
JD Processor
Woodmizer LT Super 70 and LT35 sawmill, KD250 kiln, BMS 250 sharpener and setter
Riehl Edger
Woodmaster 725 and 4000 planner and moulder
Enough cows to ensure there is no spare time.
White Oak Meadows

trimguy

 

 

 

 
Here is the tags off my 3 machines. 208v on all , and 220-230 on all. I don't know that it matters to me as long as I can get them all to work.

Southside

The only common voltage to all three is 208. The first one is 208/220  You have an alternator that is specd for 208.  I would check the taps, set it up for 208, verify voltage, and call it a day.  
Franklin buncher and skidder
JD Processor
Woodmizer LT Super 70 and LT35 sawmill, KD250 kiln, BMS 250 sharpener and setter
Riehl Edger
Woodmaster 725 and 4000 planner and moulder
Enough cows to ensure there is no spare time.
White Oak Meadows

trimguy

Quote from: moodnacreek on October 23, 2021, 09:46:16 PM
This voltage output is confusing. If it is a 208 as tagged I think 1 lead would read 110V. If it has been reconnected for 480V, one lead to neutral should read 277V.  257V is right in between and I don't think the rpm is far enough off to do that but it's not dead so there has to be a fix.
Is this right, 208v then one lead should be 110 ? Thanks southside , I hope to get a chance to mess with it today.

Magicman

Regardless of the voltage, the Hz has to be 60Hz  (cps)  and the correct RPM/load should keep it there.  The governor has to function properly.
98 Wood-Mizer LT40 SuperHydraulic    WM Million BF Club

Two: First Place Wood-Mizer Personal Best Awards
The First: Wood-Mizer People's Choice Award

It's Weird being the same age as Old People

Never allow your Need to make money
To exceed your Desire to provide Quality Service

21incher

This may not be relevant here but to check my RV generator volts and hz I had to use a meter rated for true RMS otherwise the readings were not accurate. I have no idea what the difference was.
Hudson HFE-21 on a custom trailer, Deere 4100, Kubota BX 2360, Echo CS590 & CS310, home built wood splitter, home built log arch, a logrite cant hook and a bread machine. And a Kubota Sidekick with a Defective Subaru motor.

moodnacreek

Quote from: trimguy on October 24, 2021, 06:28:48 AM
Quote from: moodnacreek on October 23, 2021, 09:46:16 PM
This voltage output is confusing. If it is a 208 as tagged I think 1 lead would read 110V. If it has been reconnected for 480V, one lead to neutral should read 277V.  257V is right in between and I don't think the rpm is far enough off to do that but it's not dead so there has to be a fix.
Is this right, 208v then one lead should be 110 ? Thanks southside , I hope to get a chance to mess with it today.
That is correct, with 208 service you get 110 off 1 lead and 208 single phase off 2 [if I remember] and 208 3 phase of all three leads. This means if you need 110 for controls or anything you don't need a transformer.

scsmith42

My advice is to fix the governor problem first, as that is most likely the source of your high voltage at low load and low voltage at high load problem.

Once the governor is operating properly you can tweak it for the proper voltage.

Personally I'd set it up for 230VAC at 60Hz.  208 will require larger wires and 220 / 230 are basically interchangeable voltages as far as the motor's are concerned.
Peterson 10" WPF with 65' of track
Smith - Gallagher dedicated slabber
Tom's 3638D Baker band mill
and a mix of log handling heavy equipment.

trimguy

The tester I picked up just happen to be a true RMS. And that's where my luck ran out. Found wiring diagram to wire to 208 bolts. I wired it up, Everything checked good. Plug the tablesaw in, Everything's good. Plug the planner in, Everything's good, RPM's dropped to 1664 and the planner was up to speed. Was checking a couple other things, the planner started to slow down, how old out to the generator it was idled down And the magic smoke was coming out of the alternator. Now it is locked up. I'm just a little ticked and frustrated with myself at the moment. I want to thank everybody that commented and give me ideas to do on this, I really appreciate it. Now I have to figure something else out I guess.

mike_belben

Sorry to hear man.  


Does it have a belt drive "hoof" governor?  
Praise The Lord

Oliver05262

I know you said the smoke was coming out of the alternator, but I would be concerned about piston damage that occurred before you found and removed that rat's nest around the cylinders. The air cooled Deutz engines do not tolerate restrictions to the air flow and I've been down that route. Got real acquainted with Mike's old employer in Ludlow, MA.
Oliver Durand
"You can't do wrong by doing good"
It's OK to cry.
I never did say goodby to my invisible friend.
"I woke up still not dead again today" Willy
Don't use force-get a bigger hammer.

mike_belben

I did work there for a spell, grew up right down the street. 
Praise The Lord

hedgerow

Quote from: Oliver05262 on October 24, 2021, 11:31:27 PM
I know you said the smoke was coming out of the alternator, but I would be concerned about piston damage that occurred before you found and removed that rat's nest around the cylinders. The air cooled Deutz engines do not tolerate restrictions to the air flow and I've been down that route. Got real acquainted with Mike's old employer in Ludlow, MA.
I totally agreed with this statement. I would hate to guess how many air cooled Deutz and Wisconsin engines I have had to overhaul because of mice nest. They don't run very long with the air fins plugged before its scored a piston and cylinder. I don't even start one that's set very long without opening up the tin on the engine. 

trimguy

Mike, I'm going to say it doesn't. Does that make it better or worse ?


I ran it a couple of times after I cleaned the rats nest out. I realize that the damage could have already been started. Maybe that's better news, the engine could be rebuilt . I don't know if that alternator can be.When I get a chance I will Separate them and see which ones locked up. I have a lot going on, probably shouldn't have taken the time to mess with it. But, I was a little excited, just wanted to run one board through